Default Off grid PV system upgrade- 12V or 24V?

Bought an off-grid home last June, all PV electricity (major appliances propane). Need to increase capacity and replace mod. sine wave inverter with pure sine wave. I have already acquired additional panels to increase my array size 50% (these are 17V panels) and 24 new 12V AGM batteries for a much larger bank. The house is wired for both 12V (DC service panel supplied directly by batteries) and 120V supplied by inverter. My question is: would I be better off leaving everything wired 12 volt and getting the highest output 12V pure sine inverter I can find, or wire the panels and batteries in 24V series pairs for a 24V pure sine inverter? If I went 24V, how would I convert to 12V to supply the DC service panel and my 12V circuits? Thanks for your suggestions.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #2  
Old 12-28-2009, 04:24 PM
indianasolar's Avatar
Administrator
Site Admin
MODERATOR
 
Join Date: Feb 2007
Location: Greenwood, Indiana
Posts: 2,251
Default

Go with 24 or 48 volts DC. The higher the voltage the lower the losses from heat. (I squared R losses)

What kind of Charge controller do you have? What is the total panel wattage?
__________________
Making the world a better place just makes sense.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #3  
Old 12-28-2009, 04:33 PM
Sunking's Avatar
Solar Nut
Solar Super Nova
MODERATOR
 
Join Date: Dec 2007
Location: Somewhere in TX
Posts: 4,136
Default

You are pretty much stuck with a 12 volt system unless you want to spend big bucks.

Option 1 is go to 24 or 48 volt battery system with an inverter to match. Then buy a 48 volt to 12 volt DC-to-DC converter. Problem is the converters are very expensive, and if we are talking about something more than say 100 to 200 watts does not exist and would be a custom manufacture meaning really big money.

Option 2 is same as option 1, except replace all your 12 volt gizmos to match the system voltage. Problem with that is most of the gizmos do not exist in 24 and 48 volt units.

Option 3 is probable the best option. go with a 24 or 48 volt system, get a larger inverter, scrap and replace all your 12 volt gizmos with 120 volt AC gizmos to run off the larger inverter.

I do have a couple of more ideas, but I have not and will not run the numbers so I am just throwing out the ideas as food for thought.

1. Build two systems. build one for the AC inverter and run the battery voltage at 24 or 48 volts. The second is a 12 volt battery system to run your 12 volt gizmos.

2. Is build one 24 or 48 volt inverter system. Then buy one of the high power 12 volt switch mode power supplies made for HAM radio operators and bench technicians. Run that off the inverter. They are available up to 12 volts at 50 amps or 600 watts.
__________________
Dereck, PE, MSEE
Moderator

Last edited by Sunking; 12-28-2009 at 04:45 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #4  
Old 12-28-2009, 04:56 PM
wy_white_wolf's Avatar
Solar Super Nova
 
Join Date: Apr 2008
Location: Wyoming
Posts: 967
Default

IMHO

Quote:
1. Build two systems. build one for the AC inverter and run the battery voltage at 24 or 48 volts. The second is a 12 volt battery system to run your 12 volt gizmos.
Might be the best way to go. I like being able to turn the inverter off at night (or whenever not needed) and still have a 12v light to get around by.
__________________
"I believe that intense beer immersion therapy is the only answer." Oggie

Al Gore - the James Baker of Enviromentalism

Every dollar spent on cutting your power usage saves $4 dollars on solar setup costs.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #5  
Old 12-28-2009, 05:46 PM
Sunking's Avatar
Solar Nut
Solar Super Nova
MODERATOR
 
Join Date: Dec 2007
Location: Somewhere in TX
Posts: 4,136
Default

FWIW I would can the AGM battery idea because they cost several times more than their flooded lead acid Brother for a given specification. AGM is only justified in mobile applications where spillage or mounting orientation is an issue, or in extreme arctic cold temperatures. Otherwise they offer no advantage in stationary applications, and/or moderate climate conditions.
__________________
Dereck, PE, MSEE
Moderator

Last edited by Sunking; 12-28-2009 at 05:52 PM.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #6  
Old 12-30-2009, 12:53 AM
n3qik's Avatar
Solar Super Nova
 
Join Date: Oct 2007
Location: Telford,Pa
Posts: 692
Default

Using AGM does have one advantage, no watering of batteries. This plus not having to vent them is why I used them.
__________________
My solar setup:
http://home.comcast.net/~n3qik
Updated 6-7-2009

Home Automation: http://68.81.42.56:5800/ Password = guest
Software/hardware 80% complete.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #7  
Old 01-14-2010, 10:53 PM
Forum Newbie
 
Join Date: Jan 2010
Posts: 7
Default

Um AGM batteries also have the advantage of being able to put them in the shack were your generator is and not have to worry about hydrogen gas popping off.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #8  
Old 01-14-2010, 11:02 PM
Sunking's Avatar
Solar Nut
Solar Super Nova
MODERATOR
 
Join Date: Dec 2007
Location: Somewhere in TX
Posts: 4,136
Default

Quote:
Originally Posted by wacnstac View Post
Um AGM batteries also have the advantage of being able to put them in the shack were your generator is and not have to worry about hydrogen gas popping off.
Gassing is not much of a problem unless your have batteries in a tightly sealed room or container with no ventilation.

AGM batteries are very expensive and best used in extreme cold, or when mounting orientation or spillage is a concern. Otherwise there is really no reason to use them unless you have money to burn.
__________________
Dereck, PE, MSEE
Moderator
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #9  
Old 01-16-2010, 03:50 AM
Forum Newbie
 
Join Date: Sep 2009
Location: Tucson, Az. USA
Posts: 13
Default

Quote:
Originally Posted by wy_white_wolf View Post
IMHO



Might be the best way to go. I like being able to turn the inverter off at night (or whenever not needed) and still have a 12v light to get around by.
Great suggestion. I prefer doing all I can everywhere 12 volt. The biggest contributing factor to success with any of these systems is leaving the inverters off. You learn that quick living with one. Think of it as a running appliance.
__________________
http://newworldsolarpower.com
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
  #10  
Old 01-19-2010, 03:14 PM
Forum Newbie
 
Join Date: Jan 2010
Posts: 7
Default

Quote:
Originally Posted by Sunking View Post
Gassing is not much of a problem unless your have batteries in a tightly sealed room or container with no ventilation.

AGM batteries are very expensive and best used in extreme cold, or when mounting orientation or spillage is a concern. Otherwise there is really no reason to use them unless you have money to burn.
The generator shack where my batteries sit is fairly well ventilated and is not at all heated. Those batteries will see temperatures that are below zero on a regular basis in the winter.
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT. The time now is 12:44 AM.


Powered by vBulletin® Version 3.8.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Optimization by vBSEO 3.5.1